losses in HVDC are purely resistive, whereas in AC circuits there are also reactive losses, especially corona effects in which the electric fields induced by the AC interact with the surrounding environment.
Resistive losses are proportional to the square of the current, so increasing the voltage for a given amount of power reduces the losses since it reduces the current. this is true for both AC and DC circuits. Inductive losses, on the other hand, are related to the electric field flux density, which increases with voltage. The reason that HVAC lines are mounted so high is to minimise corona losses due to interaction of the electric field with the ground.
There are a couple of reasons for preferring AC for local distribution, including the cost of terminal equipment and the large existing installed base of AC powered equipment. However, HVDC makes a lot of sense for distribution lines.